    hi all. if a contactor is rated at say 30A does that mean each pole is rated for 30A? or is it combined 30A. thanx alot.

  2. #2
    HB Forum Owner electric-ed's Avatar
    Join Date
    November 17th, 2001
    Posts
    191
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    Each pole is rated 30 amps.

    Ed

  3. #3
    Senior Hostboard Member Denial701's Avatar
    Join Date
    September 30th, 2022
    Posts
    178
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    1 Post(s)

    Re: lighting contactors

    Hi! If a contactor is rated at 30A, that typically means each pole is rated for 30A individually, not a combined total. So on a 3-pole contactor, each leg can handle 30A. Just make sure to check the manufacturer’s datasheet to confirm ratings for your specific model. Better just contact an electrical contractor

  4. #4
    Junior Hostboard Member Husniye's Avatar
    Join Date
    August 4th, 2026
    Posts
    1
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Re: lighting contactors

    In simple terms, a 3-pole (3P) 30A contactor means that each of its contacts is designed to handle a current of 30A. In a standard 3-phase circuit, this means it can safely control a load with a total power of approximately 30A × 3 phases = 90A.


    Understanding "Rated Current"


    Independent per pole: The ratings of most industrial contactors are for each main contact. Therefore, the 30A you see is usually the capacity per pole.


    Product labeling: Many product specifications will explicitly state "30 amps per phase" or similar wording to clarify this.


    Different application categories: The rated current of a contactor will vary depending on its application category (e.g., AC-1, AC-3). For example, a contactor might be rated 30A for resistive loads (AC-1) but a lower rating for motor loads (AC-3).
    Oyostepper supply the following products online: cnc motion controller kit, planetary gearboxes, spindle motors, and stepper motors, which can be purchased online if needed.